Travis Weimer@travisweimer· 446 views
Limit switch normal state is high
Hello all,
I am working on getting my robot up and running and did the limit switch test and all the limit switches are in the high state in the normal position and low state when the switch is activated. Reviewed all wiring and can’t find any issues. Does any one have some advice on why this is or a solution.
Thanks

Johann Voigtlander
It sounds like you wired the switches to NC (normally closed) and com.
Rewiring them to NO (normally open) should fix that.
Maybe.